Default 15 amp vs 20 amp - how do they interchange

I'm going to expose my complete lack of understanding in regards to basic electricity and it's relationship to audio, but this is my first venture into using 20 amp.

Situation:

I have a 15 amp Running Springs Haley on the way with 6 outlets. After reading a few other power related threads on here, I started to recognize the results possible with dedicated 20 amp lines. I went out to our circuit breaker and found that the microwave has a dedicated 20 amp line. The cool thing is, the box is located inside the cabinets above the range hood....and the kicker...the box is perfectly located on the same wall (other side) to my system. So, it would be as easy as punching a hole through the hidden drywall on the kitchen side, dropping a 3 meter cord straight down, punching a hole in the listening room side, and plugging it into the Haley. I can plug the microwave into another 20 amp socket (although not dedicated) and voila, I have a dedicated 20 amp line in a rental house without having to call out the electrician.

So, the questions:

Any issue with plugging the 15 amp Haley into the 20 amp outlet?

If the above situation is a non issue, How would you configure my MC275, C2300, and MVP 881? All into the Haley? Or maybe get a high quality power strip that is getting the feed from the direct 20 amp and plug the Haley into it. Then the 2300 and 881 go into the Haley and the 275 goes directly into the power strip.

Ignore the equipment in my signature, it's all in a state of major overhaul.

Thanks in advance!

Brent
__________________
Brent
Equipment: McIntosh MC302, McIntosh MX121, Franco Serblin Accordo, Oppo 105 Darbee Modwright, Running Springs Haley
Cables: Wireworld Gold Eclipse speaker, Wireworld Gold Eclipse Interconnects, Wireworld Silver Power Cords
Reply With Quote
  #2  
Old 01-01-2014, 03:56 PM
Mikado463 Mikado463 is offline
Guest
 
Join Date: Aug 2011
Location: SE Pa
Posts: 3,925
Default

punching holes, running cords through walls (absolute no-no), all of which I'm not sure of what you're trying to say.

Here's the simple answer, get a qualified electrician and run a dedicated 20 amp service from your breaker box to your audio……..while your at it…run two !
Reply With Quote
  #3  
Old 01-01-2014, 04:15 PM
jdandy's Avatar
jdandy jdandy is offline
Merry Christmas to all



 
Join Date: Apr 2009
Location: North Central Florida
Posts: 53,224
Default

Brent.......The idea has merit, unfortunately what you want to do is against the National Electrical Code which requires a fixed appliance (microwave) to be on a dedicated circuit, not a shared circuit. In addition to that code requirement, any power cords installed inside a wall must be rated for such installation.

You may remember my comment about liability from adding a circuit to property that does not belong to you. You are increasing your exposure with additional liability by performing any electrical work that does not comply to NEC requirements or flagrantly violates these regulations. Ask yourself this, can I personally pay for any damage to this apartment or the entire building? Furthermore do you wish to be held directly responsible for any loss of life should a catastrophe take place from the electrical alterations you performed? It would not take a savvy insurance investigator long to figure out the cause of a fire from a jury-rigged circuit if it should go up in flames. Electricity can be very dangerous and destructive. Only a qualified licensed electrician should be allowed to make changes or additions to an electrical system.
__________________
Dan



STUDIO - McIntosh C1000C/P, MC2301 (2), MR88, Aurender N10, Esoteric K-01X, Shunyata Sigma spdif digital cable, Sonos Connect, PurePower 2000, Stillpoints, Furutech Flux 50, Michell Gyro SE, Michell HR Power Supply, SME 309, Ortofon Cadenza Black, Wireworld, Sonus faber Amati Anniversario
LIVING ROOM - McIntosh C2300, MC75 (2), MR85, Magnum Dynalab 205, Simaudio MOON Neo 260D-T, Schiit Audio Yggdrasil, Aurender N100H, Shunyata Sigma USB cable, Micro Seiki DD40, Ortofon Cadenza Blue, Nakamichi BX-300, Sony 60ES DAT, PS Audio P10, Furutech Flux 50, Sonos Connect, Stillpoints, Wireworld, Kimber, PMC EB1i, JL Audio f113
VINTAGE - McIntosh MA230, Tandberg 3011A tuner, Olive 04HD, Sony DTC-59ES DAT, McIntosh 4300V, JBL 4312A
Reply With Quote
  #4  
Old 01-01-2014, 05:47 PM
cma29's Avatar
cma29 cma29 is offline
Member
 
Join Date: Apr 2013
Location: Columbia, Missouri, USA
Posts: 4,405
Default

Quote:
Originally Posted by jdandy View Post
Brent.......The idea has merit, unfortunately what you want to do is against the National Electrical Code which requires a fixed appliance (microwave) to be on a dedicated circuit, not a shared circuit. In addition to that code requirement, any power cords installed inside a wall must be rated for such installation.

You may remember my comment about liability from adding a circuit to property that does not belong to you. You are increasing your exposure with additional liability by performing any electrical work that does not comply to NEC requirements or flagrantly violates these regulations. Ask yourself this, can I personally pay for any damage to this apartment or the entire building? Furthermore do you wish to be held directly responsible for any loss of life should a catastrophe take place from the electrical alterations you performed? It would not take a savvy insurance investigator long to figure out the cause of a fire from a jury-rigged circuit if it should go up in flames. Electricity can be very dangerous and destructive. Only a qualified licensed electrician should be allowed to make changes or additions to an electrical system.
Great advice, Dan.

The NEC is a standard published by the National Fire Protection Association (NFPA) so what Dan is saying about a fire catastrophe caused by non-compliant wiring rings the bell.
Reply With Quote
  #5  
Old 01-01-2014, 06:14 PM
Bikeman71's Avatar
Bikeman71 Bikeman71 is offline
Senior Member
 
Join Date: Mar 2013
Location: Pollock Pines, CA
Posts: 383
Default

Thanks, guys! I knew this was the right place to ask. I guess my mistake was not seeing the difference between a 3 meter WW silver cable on the floor as opposed to having a section in-between the drywall.. What about the common practice of TV power cords being run into the wall at the unit and back out near the floor to hide all the cords. Is this also a no-no?

So, what about the 15 amp RS Haley plugged into a 20 amp socket. Benefits?
__________________
Brent
Equipment: McIntosh MC302, McIntosh MX121, Franco Serblin Accordo, Oppo 105 Darbee Modwright, Running Springs Haley
Cables: Wireworld Gold Eclipse speaker, Wireworld Gold Eclipse Interconnects, Wireworld Silver Power Cords
Reply With Quote
  #6  
Old 01-01-2014, 06:20 PM
cma29's Avatar
cma29 cma29 is offline
Member
 
Join Date: Apr 2013
Location: Columbia, Missouri, USA
Posts: 4,405
Default

Quote:
Originally Posted by Bikeman71 View Post
Thanks, guys! I knew this was the right place to ask. I guess my mistake was not seeing the difference between a 3 meter WW silver cable on the floor as opposed to having a section in-between the drywall.. What about the common practice of TV power cords being run into the wall at the unit and back out near the floor to hide all the cords. Is this also a no-no? So, what about the 15 amp RS Haley plugged into a 20 amp socket. Benefits?
Plugging a 15-amp device into a 20-amp socket should be ok. Essentially you'll have spare current capacity which is fine. Think of amperes as the amount of water flowing through a pipe. With 20 amps the "pipe" has a bigger diameter and thus can carry more water even if you don't need all of it.

What you don't want to do is to plug a 20-amp device into a 15-amp socket because the circuit will overload and in a worst case scenario, overheat and possibly cause a fire.

Last edited by cma29; 01-01-2014 at 07:21 PM.
Reply With Quote
  #7  
Old 01-01-2014, 08:46 PM
jdandy's Avatar
jdandy jdandy is offline
Merry Christmas to all



 
Join Date: Apr 2009
Location: North Central Florida
Posts: 53,224
Default

Brent.......An alternative has come to mind. If the circuit to the microwave junction box is in conduit back to the panel, you could have an electrician fish in an additional circuit through that conduit to the microwave junction box, then have the remaining length of the dedicated circuit routed from their to where you need it using metal clad wire (MC cable) to the dedicated outlet location. MC cable is rated for in-wall installation. You will still be adding a circuit to an apartment that is not yours but at least the installation will then meet code.
__________________
Dan



STUDIO - McIntosh C1000C/P, MC2301 (2), MR88, Aurender N10, Esoteric K-01X, Shunyata Sigma spdif digital cable, Sonos Connect, PurePower 2000, Stillpoints, Furutech Flux 50, Michell Gyro SE, Michell HR Power Supply, SME 309, Ortofon Cadenza Black, Wireworld, Sonus faber Amati Anniversario
LIVING ROOM - McIntosh C2300, MC75 (2), MR85, Magnum Dynalab 205, Simaudio MOON Neo 260D-T, Schiit Audio Yggdrasil, Aurender N100H, Shunyata Sigma USB cable, Micro Seiki DD40, Ortofon Cadenza Blue, Nakamichi BX-300, Sony 60ES DAT, PS Audio P10, Furutech Flux 50, Sonos Connect, Stillpoints, Wireworld, Kimber, PMC EB1i, JL Audio f113
VINTAGE - McIntosh MA230, Tandberg 3011A tuner, Olive 04HD, Sony DTC-59ES DAT, McIntosh 4300V, JBL 4312A

Last edited by jdandy; 01-01-2014 at 08:56 PM.
Reply With Quote
  #8  
Old 01-22-2014, 04:10 PM
kamiraa kamiraa is offline
Senior Member
 
Join Date: Mar 2013
Location: Austin, TX
Posts: 251
Default

Quote:
Originally Posted by cma29 View Post
Plugging a 15-amp device into a 20-amp socket should be ok. Essentially you'll have spare current capacity which is fine. Think of amperes as the amount of water flowing through a pipe. With 20 amps the "pipe" has a bigger diameter and thus can carry more water even if you don't need all of it.

What you don't want to do is to plug a 20-amp device into a 15-amp socket because the circuit will overload and in a worst case scenario, overheat and possibly cause a fire.
In regards to safety, that's what breakers are for. If you plug a 20 amp device into a 15 amp one, you MAY trip the breaker. It just depends how much current the 20 amp device is actually going to demand upon startup and use. Overall, its just a bad idea, but if your breakers are sized per the wiring you will not have a safety concern.

Now as for plugging a 15 amp device into a 20 amp outlet. It's a GREAT idea. Here is the reasoning, your 20 amp circuit needs to be wired with higher gauge wiring from the service breaker box. So you will have higher current capacity on that wiring for peak demands.

The same way a lot of people spend THOUSANDS of dollars for cabling from the wall to the audio device, you should think about the other side of the circuit (behind the wall).

The outlet to breaker (behind the wall) should be comprised of cable greater than or equal to the power cord you are installing from the outlet to device, or you are just wasting your time.

For example, if you go install a very nice power cord that is 10 gauge effective size, you should make sure your wiring behind the wall is 10 gauge or bigger (8, 6, etc). Otherwise the benefit is diminished.

I've seen a lot of people run these massive cords in older style homes which it's guaranteed the in wall cabling is junk (small gauge or bad material).

One of the best things anyone can do to establish their audio system is have an electrician come out and run new and extremely thick gauge power cable as a "home run". This means direct from the breaker to the room, with no intermediate paths. Finish up the termination with a higher end outlet to maintain the integrity of the electrical path. Then use higher end cabling.

Such a small change can make a massive difference to your electrical integrity.

If you want to go one step further, you can install a new sub-panel, and keep all noisy loads (fans, air conditioning, microwave, refrigerators, lighting, etc) off it.

Last edited by kamiraa; 01-22-2014 at 04:12 PM.
Reply With Quote
  #9  
Old 01-23-2014, 07:40 PM
rlw3 rlw3 is offline
Senior Member
 
Join Date: Jul 2012
Location: east bay ca
Posts: 616
Default

My new 20 amp line sounded bad when brand new. I used a big fan while at work for several hundred hours because it was easy to do
Reply With Quote
  #10  
Old 01-25-2014, 02:17 PM
Allan W. Allan W. is offline
Senior Member
 
Join Date: Jun 2011
Location: Southern Nevada
Posts: 182
Default

Do yourself a favor. If you have a questions regarding your homes electrical system consult an Electrical Professional, such as a local Licensed: Electrician, Electrical Contractor or Electrical Engineer.
__________________
Amps: VTL 450MKII, Speakers: B&W 801S-3, Full Function Pre-Amp: McIntosh C-2500, Multi-Format Digital Disc Player: Esoteric DV-50. Hard Drive Based Digital Playback: Mac Mini w/Esoteric D-07 DAC. Vinyl Playback:Technics SL-1210MKII w/Jelco 750 arm , Denon DL-103r w/hardwood body and Denon DP-500M w/Jelco 750 arm and AT-14sa. Power and Cabling: PS Audio Power Plant Premier, Cabling=various mid level MIT.
Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Audioaficionado.org tested by Norton Internet Security

All times are GMT -4. The time now is 09:56 AM.



Powered by vBulletin® Version 3.8.10
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
©Copyright 2009-2023 AudioAficionado.org.Privately owned, All Rights Reserved.
Audio Aficionado Sponsors
AudioAficionado Subscriber
AudioAficionado Subscriber
Inspire By Dennis Had
Inspire By Dennis Had
Harmonic Resolution Systems
Harmonic Resolution Systems
Wyred4Sound
Wyred4Sound
Dragonfire Acoustics
Dragonfire Acoustics
GIK Acoustics
GIK Acoustics
Esoteric
Esoteric
AC Infinity
AC Infinity
JL Audio
JL Audio
Add Powr
Add Powr
Accuphase - Soulution
Accuphase - Soulution
Audio by E
Audio by E
Canton
Canton
Bryston
Bryston
WireWorld Cables
WireWorld Cables
Stillpoints
Stillpoints
Bricasti Design
Bricasti Design
Furutech
Furutech
Shunyata Research
Shunyata Research
Legend Audio & Video
Legend Audio & Video